jeff43222
Senior Member
- Location
- Minneapolis, Minnesota
I recently did a service upgrade for a guy, and part of the deal is that he wants me to install new circuits for the dryer, laundry, and water heater. I took a look at the water heater the plumber installed the other day, and I discovered that it was a gas model, with 120V electricity needed just to power the electronic ignition.
The HO told me that the plumber was adamant that the receptacle had to have GFCI protection, but I told the HO that apart from being a bad idea overall, I said the only reason I could see it being necessary is if the instructions said it had to have it (receptacle is more than 6' from the utility sink).
So I looked through the instructions, only to discover that they stated very clearly that they do NOT recommend GFCI protection for the receptacle. Since it's not required, I told the HO that I'd put in a single non-GFCI receptacle for it. He was pretty happy I caught the plumber's error, particularly when I explained why I didn't think GFCI protection was a good idea in this case.
Moral of the story: Don't rely on the plumber to get advice about electrical requirements.
The HO told me that the plumber was adamant that the receptacle had to have GFCI protection, but I told the HO that apart from being a bad idea overall, I said the only reason I could see it being necessary is if the instructions said it had to have it (receptacle is more than 6' from the utility sink).
So I looked through the instructions, only to discover that they stated very clearly that they do NOT recommend GFCI protection for the receptacle. Since it's not required, I told the HO that I'd put in a single non-GFCI receptacle for it. He was pretty happy I caught the plumber's error, particularly when I explained why I didn't think GFCI protection was a good idea in this case.
Moral of the story: Don't rely on the plumber to get advice about electrical requirements.