So, here's a weird one (at least for me). I was called to a house for a hairdryer tripping the breaker. When I opened the receptacle boxes in the bathroom, every single box had dangerously loose connections (both wire nut and wire->device connections). After fixing those, the customer and contractor wanted me to go through the whole house and check switch and receptacle boxes for more. Probably about 75% of the boxes in the house had loose/bad connections or other problems (like the back of a receptacle box cut off to make it fit in a smaller space or the N/G for the living room circuit being tapped off the furnace circuit instead of the living room). Also about half the AFCI and combo breakers in the panel had the arc and ground fault protection bypassed by running the neutral wire straight to the neutral bar and capping off the pigtail. I've got all the breakers wired back up properly, but now I can't get the arc fault breakers to trip properly. I can trip them with the test button, but if I touch the ground and neutral together, nothing happens. Normally, that's an instant trip. I've even used a jumper wire in the panel from N lug on the breaker to the ground bar to see if I could trip it that way. All the troubleshooting discussions I see are on what to do with arc faults tripping too often, but had anyone dealt with ones that won't trip at all?