Your taking me all wrong on this.
The way I see it is once the wiring is terminated and the wiring is installed there's never really a need to disturb the connection or the device unless something goes wrong.
I dont see much vibration that would accidently make the neutral come in contact with the ground wire if the wires were seperated enough on installation.
so then it falls back to the wires not being seperated enough in the box to begin with.
Accidental ground to neutral contacts I can see,
For instance I troubleshot a tripping arc fault the other night becauise when the customer replaced the lamp in the vanity fixture the Neutral shell of the socket twiisted over and made
contact with the metal housing. (Cheap Fixture). I can see that, but it shouldnt happen very often in the house wiring just because the Neutral and Ground connections are on the same side.
Experienced guys like myself have learned to watch for these problems when installing a receptacle. The new guy that was just hired has not had to rework as many failed installations and will make those mistakes. Also the guy that has not had to deal with AFCI's before has one other potential device to catch mistakes he was overlooking before. True similar mistakes could be made on GFCI protected outlets, but there was probably less GFCI feed through protected receptacles than there is AFCI protected devices so there will be a higher risk of making a mistake. The GFCI may only feed an additional outlet or two in many cases, the AFCI is protecting the entire circuit (at least until these new wall box AFCI devices become more common in use).