The question of " why is the afci tripping " comes up on the forum often so I thought I would share a "nuisance tripping" that I traced out today.
A home owner who's remodel I wired about a year ago called and explained that the bedroom AFCI circuit had shut off multiple times over the last year. They would reset the breaker and it would be fine for a while. Until today, it would not reset. So I went through all the basic steps disconnecting all loads, opening up boxes etc. There were no obvious problems everything was wired correctly. Using an ohm meter there was no apparent problems or shorts. So I ran a megger test on the line and found a neutral to ground fault that only shows up when the voltage starts getting up in the 270 volt range.
The problem turned out to be when the carpenters put in some blocks for sheet rock backing they pinched an NM cable in the wall against its staple. This caused a small split , maybe 1/16th" , in the insulation on the neutral wire this bare spot would connect with the ground intermittently and trip the afci.
Had this of been a non-afci circuit it would have never shown up as a problem. If I had not used a megger on the circuit I would have never been able to locate the exact place in the line that had failed.
A home owner who's remodel I wired about a year ago called and explained that the bedroom AFCI circuit had shut off multiple times over the last year. They would reset the breaker and it would be fine for a while. Until today, it would not reset. So I went through all the basic steps disconnecting all loads, opening up boxes etc. There were no obvious problems everything was wired correctly. Using an ohm meter there was no apparent problems or shorts. So I ran a megger test on the line and found a neutral to ground fault that only shows up when the voltage starts getting up in the 270 volt range.
The problem turned out to be when the carpenters put in some blocks for sheet rock backing they pinched an NM cable in the wall against its staple. This caused a small split , maybe 1/16th" , in the insulation on the neutral wire this bare spot would connect with the ground intermittently and trip the afci.
Had this of been a non-afci circuit it would have never shown up as a problem. If I had not used a megger on the circuit I would have never been able to locate the exact place in the line that had failed.