At least one of them at/near 0.
A=30
B=15
C=15
N=15
A=30
B=15
C=0
N=26
A=30
B=30
C=0
N=30
Be careful presenting examples like I do.
Infinity might compare you to a dog chasing his tail.....
JAP>
At least one of them at/near 0.
A=30
B=15
C=15
N=15
A=30
B=15
C=0
N=26
A=30
B=30
C=0
N=30
At least one of them at/near 0.
A=30
B=15
C=15
N=15
A=30
B=15
C=0
N=26
A=30
B=30
C=0
N=30
I'm also questioning that extra amp in example #2.
JAP>
I'm also questioning that extra amp in example #2.
JAP>
When you round up that's correct.
JAP>
When someone thinks this ... maybe it is?Folks, overcurrent was and is irrelevant to the topic.
It takes all of the single pole breakers to protect that neutral; if any one of them fails to trip on overcurrent, then an overcurrent on the associated ungrounded conductor would overload that neutral.
Folks, overcurrent was and is irrelevant to the topic.
This whole topic seems irrelevant seeing as how there hasn't been an answer that everyone will agree on.
JAP>
That doesn't mean it hasn't given me useful information.
One cannot use single pole AFCIs with handle ties .... unless they don't have GFCI functionality? (Which breaker would you land the neutral on?) Does anyone besides GE make these?
I believe that's what I said, although perhaps not as clearly.Actually, the overloaded phase that lost it's OCP is what is overloading the neutral.
The relevancy is that the phrase "overcurrent device protecting the circuit" appears in the definition of Branch Circuit.Folks, overcurrent was and is irrelevant to the topic.
I believe that's what I said, although perhaps not as clearly.
Cheers, Wayne
Have you ever measured the voltage of the derived "third phase" of a rotary phase converter? It is never even close to same volts to neutral as the input conductors.In that case, there's your AFCI workaround: get a large rotary phase converter and run all your circuits from a 3 phase panel.
Seriously, with a GE or BR panel, there are AFCIs without GF detection, so you could run a 3-phase MWBC for 120V loads with 3 single pole AFCI breakers and a handle tie. [I'm assuming that GE or BR make a 3-phase panel that accepts those breakers.]
Cheers, Wayne
But, as a delta source, they're relatively close.Have you ever measured the voltage of the derived "third phase" of a rotary phase converter? It is never even close to same volts to neutral as the input conductors.
But, as a delta source, they're relatively close.
Rotary phase converter line to line voltages are definitely better than what you usually see from a static converter. Somewhat is dependent on connected load in either case.
That is correct. No manufacture sells a common trip 3-pole combination-type AFCI.No one makes a 3-pole AFCI, right?
Sq D's 2-pole combination-type AFCI installation instructions clearly state the breaker is NOT to be installed on 208 / 120 V 3-wire single phase.If one wants to use a 2-pole AFCI on a 3 wire MWBC, will it work on a 120/208 circuit? Or does it depend on the brand?
This is true for Siemens, Sq D and Eaton CH breakers.One cannot use single pole AFCIs with handle ties .... unless they don't have GFCI functionality?
GE combination-type AFCI single pole breakers are allowed to be installed WITHOUT the load neutral landing on any of the handle tied breakers.(Which breaker would you land the neutral on?)
NO.Does anyone besides GE make these?