jaggedben
Senior Member
- Location
- Northern California
- Occupation
- Solar and Energy Storage Installer
Is this thread about to die? We haven't even discussed yet why 210.12 says 'single phase'?
Each circuit is single phase.Is this thread about to die? We haven't even discussed yet why 210.12 says 'single phase'?
Nooooooooooooooooooo! :happysad: :happysad: :happysad:Was that an attempt to drag in the classic single phase versus two phase dispute for 120/240?
Any single-phase outlet an any of the above. It's the outlet that triggers the requirement.Poll:
Which of the following require arc-fault protection in dwellings? (Check all that apply.)
- a 120/240 3-wire MWBC
- a 120/208 3-wire MWBC
- a 120/208 4-wire MWBC*
Any single-phase outlet an any of the above. It's the outlet that triggers the requirement.
Not as far as I can tell; as you pointed out, it says "single pole", and I don't know.Wouldn't I need a 3-pole AFCI for the 4-wire, and doesn't that not exist?
AFAIK Square D 2 pole AFCI's do not work on 120/208 3 wire MWBC's either, so with a 208/120 supply you can not use MWBC's if AFCI protection will be required. Not sure about other's two pole units but can see them having similar issues.Wouldn't I need a 3-pole AFCI for the 4-wire, and doesn't that not exist?
AFAIK Square D 2 pole AFCI's do not work on 120/208 3 wire MWBC's either, so with a 208/120 supply you can not use MWBC's if AFCI protection will be required. Not sure about other's two pole units but can see them having similar issues.
My provisional position is that no MWBCs require AFCI. We've already had the discussion regarding an MWBC protected by a single multi-pole breaker. So that leaves the case of an MWBC protected by multiple single-pole breakers.Which of the following require arc-fault protection in dwellings? (Check all that apply.)
- a 120/240 3-wire MWBC
- a 120/208 3-wire MWBC
- a 120/208 4-wire MWBC*
Wouldn't I need a 3-pole AFCI for the 4-wire, and doesn't that not exist?
It takes all of the single pole breakers to protect that neutral; if any one of them fails to trip on overcurrent, then an overcurrent on the associated ungrounded conductor would overload that neutral.
if any one of them fails to trip on overcurrent, then an overcurrent on the associated ungrounded conductor would overload that neutral.
It takes all of the single pole breakers to protect that neutral; if any one of them fails to trip on overcurrent, then an overcurrent on the associated ungrounded conductor would overload that neutral.
Actually, the overloaded phase that lost it's OCP is what is overloading the neutral. The higher the amperage on the other 2 phases the lower the shared neutral current would be.
If all 3 ungrounded conductors failed to trip the OCP, the neutral might never see an overloaded condition, it depends on the loading.
to throw a wrench into this - at some point in the circuit most MWBC downstream are only a 2 wire circuit both H and N see the total load unless shorted to ground.
Just saying.hmy:
to throw a wrench into this - at some point in the circuit most MWBC downstream are only a 2 wire circuit both H and N see the total load unless shorted to ground.
Just saying.hmy:
That would be past the point of the "shared" neutral of a MWBC.
I would think the current of the remaining 1 or 2 circuits would have to be at zero for the shared neutral to receive the full return current of the overloaded circuit.
JAP>