• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

AFCI Test Button - What does it do?

Status
Not open for further replies.

ELA

Senior Member
Occupation
Electrical Test Engineer
This post was made to add to a discussion that has come up from time to time as to what an AFCI breaker does when its test switch is pushed. Many here are familiar with what the GFCI test switch does but I have not seen anything on the test function of the AFCI.

I have read several articles on the AFCI but have been unable to get great detail or much of anything about how the test switch worked.

In an attempt to gain some understanding I disassembled a QO115AFCI and began examining the circuits inside and performing tests. My intent is to share experimentally derived information about the inner workings of the one particular AFCI that I examined. I do not claim to be an expert on AFCIs nor do I hold that all of my work is flawless or 100% accurate.

Here is a photo of the AFCIs insides:

AFCIs.jpg


Click for large version

The black coil on the center right may be referred to as the “Injection/arc sense” coil. The white coil to the right will be referred to as the “leakage sense” coil.
As seen in the picture only the red wire “hot” is inside of the black core. Both the hot and the neutral wires are inside of the leakage detect core.

The black coil has two windings measured at roughly a 7:1 (dc resistance) ratio. A partial schematic below shows that one winding (bc) is used to inject a signal for test purposes. This coil connects to pin 8, an output, of the microcontroller. The other coil (ab), with a higher winding count senses current in the hot conductor , or currents injected by the injection coil.

injection_arc_sensecoil.jpg


The test button is simply an input to the microcontroller. When the test button is pushed the microcontroller does not produce a “true arc fault condition”. Instead it “injects signals” into the (bc) winding of the black coil. The signals injected there are then coupled into the (ab) winding. Several op-amp filters are connected to the (ab) winding that then feed multiple inputs to the microcontroller for analysis.

Since it would be prohibitive for this device to produce an actual high current arc it instead tests its ability to sense certain frequencies that are used in the analysis of an arc signature. Since this black core is crucial to the ability to sense an arc fault the integrity of it is what is tested. It was found that when the black coil was physically removed from the circuit board that the circuit breaker test button would no longer work (indicating a problem). However I could remove the red wire from the middle of the core and the breaker would still test ok!


The output of the microcontroller that feeds the (bc) coil was then monitored while the test button is pressed and the results are shown below:
SelfGeneratedTestSignal.jpg


When the test button of the AFCI is pressed the microcontroller outputs this waveform from pin 8 that lasts approximately 25 milliseconds.

From this it can be seen that the microcontroller puts out three distinct frequencies. First it outputs a signal at approx. (1Khz) , it then changes to a higher frequency of approx. (10Khz) , and finally back down to (2.5Khz).
Each frequency band lasts for 1/3 of the total or equal to a one-half cycle duration at 60hz.

This sequence lasts for 25 milliseconds and the breaker then trips. Note this is less than the 5 half- cycles I have read were required as a minimum to sense a true arc.

Based on this limited data, on this one product example, it appears that the test button confirms the integrity of its internal circuitry by simulating the high frequency aspects of a true arc.

It then couples these high frequencies into its sense circuitry to assure that those circuits are capable of registering the high frequency content of an arc.

I performed a lot more testing after this to the point where I was able to simulate an arc and trip the breaker. I could share more if there is any interest.
I am afraid I may have already put too much into one posting and bored you all :smile:
 
Last edited by a moderator:

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
It looks like it would be easy to convert one of these breakers into a shunt-trip breaker, if one were so inclined.
 

Buck Parrish

Senior Member
Location
NC & IN
I have changed lights for years by just turning the switch off. Now with AFCI, even with the switch off it will trip the breaker. Neutral to ground I guess.
 

cadpoint

Senior Member
Location
Durham, NC
I don't know if the Line diagram is correct to the picture, as presented.

The white barrel you show in diagram but isolated but is electrically shown interconnected in the picture.

Is the Test botton via the picture is a dual use application, releasing off the Ground screw to swing or slap the other plate or move in this gap in the plate or insure moment of the white barrel, A charged rod into a magnetic field, I don't, I have to study this more later, and as usuall read more.
 

ELA

Senior Member
Occupation
Electrical Test Engineer
I don't know if the Line diagram is correct to the picture, as presented.

The white barrel you show in diagram but isolated but is electrically shown interconnected in the picture.

Is the Test botton via the picture is a dual use application, releasing off the Ground screw to swing or slap the other plate or move in this gap in the plate or insure moment of the white barrel, A charged rod into a magnetic field, I don't, I have to study this more later, and as usuall read more.

Cadpoint,
Your comments are tough to follow?

It is difficult to see in the picture but the green screw does not have anything to do with the test switch.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
It is difficult to see in the picture but the green screw does not have anything to do with the test switch.
Agreed; it appears to be an adjustment screw.

The button spring looks to be a contact, labeled J8 on the PCB.
 

wptski

Senior Member
Location
Warren, MI
The following is a capture of the AFCI test feature of the Ideal 61-165 Suretest. This is only a part of entire test which lasted 126.4ms if I remember correctly.

61-165_AFCI_1.jpg
 

cadpoint

Senior Member
Location
Durham, NC
Look at the wires look at your diagram, The white objects power looks like the key!

Frankly in respects to your diagram the "trigger" looks engaged at three points not in series as shown in your line diagram.
Again, It looks like your diagram is more parellel than in series that use
these component devices.

The white wire is what will see the induction of the AF, the coil in front of that is the base line coil to cause everything else.

I might be totally wrong!

Where's the power coming from or goes to, you can't float the coil as you showed it cause it doesn't look like the photo.

Ode to Dad, he always stressed the "Road map of electronic's" if you can't get there, well you just can't. Can I bank on a draftsman eye, well it's been awhile!

Sorry, I'm so stark! ...
 

ELA

Senior Member
Occupation
Electrical Test Engineer
I must apolgize for the reduntant introductions in my original post.

To the moderators I ask, can the redundant introductory statements be removed? I seem to be unable to edit my original post.

Cadpoint,
I am still unsure of the point you are making?
My diagram was purposely only a partial schematic showing the points I was referring to in my text. The latch coil is of course connected in reality.

I was not my intent to address either the latch or the mechanical trip mechanism.

My thanks to Wptski for his post of an actual waveform signature as generated by his Ideal test instrument.

I found it interesting to see both the waveform magnitude and duration.
 

iwire

Moderator
Staff member
Location
Massachusetts
I must apologize for the redundant introductions in my original post.

To the moderators I ask, can the redundant introductory statements be removed? I seem to be unable to edit my original post.

I will be glad to help you out but I am not sure what you want down.

Send me a PM with the revisions and I can take care of it.

Thanks for posting all this, I think it is great and not something that I have seen posted before. :cool:
 

ELA

Senior Member
Occupation
Electrical Test Engineer
Agreed; it appears to be an adjustment screw.

The button spring looks to be a contact, labeled J8 on the PCB.

Larry,

The green screw does look to be an adjustment for the thermal trip mechanism of the breaker.

One of the interesting things I found while looking inside this breaker was that the instantaneous trip sense is electronic and not a magnetic coil.

The button spring is part of the test switch mechanics.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
090308-1242 EST

ELA:

Could you scale down your photo slightly and ask a moderator to replace the current photo. I operate at 1024 wide and therefore have to scroll sideways. Thus, very difficult to follow the written material.

.
 

M. D.

Senior Member
Thanks for sharing ,..I only wish I understood more of it :-? I need to learn more,..

Why am I reminded of Mr Scott,...

"It's armed now. Press this one, 30 seconds later, POOF! Once its activated, there's no way to stop it."
 
Status
Not open for further replies.
Top