luke warmwater
Senior Member
Re: AFCI testers
the above post that I was referring to stated that there was a multi-wire circut ran to the bedrooms, "...one neutral (with black, red ,and green)"
The problem could be solved with the proper AFCI breaker (as Kirk stated bove, Cutler Hammer makes this breaker)
Also, the post stated, "...they placed the AFCI neutral to the neutral bus, along with the multiwire neutral".
This could be solved by a simple correction.
I don't see why all 300 bedrooms had to be rewired.
Allen,Originally posted by a.wayne3@verizon.net:
Two seperate AFCI circuits can`t share one commom neutral without tripping (when there is a load on them)That is why there is 14-2-2 NM.Same as an AFCI circuit neutral being tied in downstream with the neutrals of a non AFCI circuit.That`s a BIG TRIP GOOD BUDDY.
the above post that I was referring to stated that there was a multi-wire circut ran to the bedrooms, "...one neutral (with black, red ,and green)"
The problem could be solved with the proper AFCI breaker (as Kirk stated bove, Cutler Hammer makes this breaker)
Also, the post stated, "...they placed the AFCI neutral to the neutral bus, along with the multiwire neutral".
This could be solved by a simple correction.
I don't see why all 300 bedrooms had to be rewired.