I am very familiar with those documents...
There design was a lot more user friendly, and it did open the door for the ability to allow very complex logic and self diagnostic abilities through its interface. Its a shame it was not refined upon.
I get the manufactures are part of NEMA, but I don't believe that the issue. The part that concerns me is CMP allowing AFCI requirements into the code.
Look I am not blind to some potential issues...
Its good that you have no had problems, but others are having many. The technology is imperfect for the same reason as others have stated earlier: it is to premature. The used to detect arcs is logic is to primitive.
I have no doubt that in testing AFCIs perform as indeed. I know they do so since no UL label would exist on them. But the real world is not a laboratory, and as far as I know there is no testing outside of manufacturing facilities that actively make sure AFCI will not nuisance trip.
Sure the AFCI gets a UL label because it passes tests, but what verification sticker exists to say these devices will not trip on a UL listed plasma TV or vacuum cleaner? None.
In terms of the GFI (GFP), it is assumed that because it has a protective theory of it's intended use, to protect the volitive circuitry in the devices themselves that it does add to the overall fire protective safety of the device.
Explain, that is simply so untrue. No offence but that discredits a lot of what you have said. How does differential logic protect the circuitry within the device?
Deferential logic plays a
profound role in fire safety within a branch circuit. Literally half of an AFCIs protective features are obtained via 30ma protection. A hot to ground fault, a neutral to ground fault and crossed circuits; from wiring errors, compromised insulation, over driven staples, ect produce a current differential. It does not even matter if this current difference has an arcing signature or not. Its a fire hazard. If current is leaking to the equipment grounds then a hazard along with a code violation is taking place. I can not even think of one instance where 30 milliamps and over of current leakage is allowed or normal on a branch circuit. Consider the fact that about 90% faults are hot to ground, thus the brunt of fire protection is done via differential. Same for the majority of NEC wring errors like crossed circuits: detected by GFP.
In fact, the 30ma logic allows for passing of about half the UL tests and I have heard that is actually the reason why AFCI makers put it in there to start with. As soon as the test places current on the EGC the device trips, and no arc logic is necessary to accomplish that. This guarantees a 100% chance of passing without needing to design logic specifically for that part of the test. Heck if one gave a GFCI breaker to be run through those tests it would pass about half of them.
Arc logic is only placed in AFCIs where GFP reaches its limitations. Those are parallel hot to neutral faults and low level arcing in series with the load. Of note, if one set the instantaneous magnetic trip low enough on a breaker, you could probably pass a series arc test. But in case, the goal of arc logic is to catch these.
It is true that some manufactures like GE have taken GFP out of AFCIs, but that is only to facilitate their use in MWBC and reduce customer complaints of tripping caused by electrician wiring errors. Which I do find ironic CMP is not concerned about those, ie they aren't requiring 30ma protection for AFCIs. An AFCI without GFP will let a standing neutral to ground fault continue as well as crossed circuits which are hazards in themselves. For starters, the inductive heating in ferromagnetic conduits (as well as any lose conduit connections that may spark) caused by this objectionable current is a fire hazard.
Well i will buy into the fact and even remove the assumed portion; yet UL is a paid association now who is charged with evaluating products for their intended use and currently under UL 1699 the GFI component is not required because it plays no role in the intended function of the product. While some manufacturers did (and some still do possibly) rely on this feature to pass the complete testing procedure for UL 1699 compliance others have obviously developed a method that passes without the GFI (GFP) function. What you are presenting is that experts believe that the GFI (GFP) function is a critical component that must be included and that when manufacturers leave that out they are some how immoral or pandering to the cost of production so I need to address that.
You are correct, UL does not require it and manufactures do indeed use GFP as a way to pass some tests worry free. I get that.
In purely detecting arcs GFP is not essential, however I can think of a slew of code violations some even fire hazards that arc detection will not pick up on where GFP will catch it immediately.
The issue is not that manufactures are taking out something that's not required but rather the fact the CMP is not mandating it.
The NEC clearly states that an electrical system shall be free of defects and errors, but how do we know that? We don't unless we test the installation or even better have an OCPD that picks up on it. How many North American electricians test circuits? None. How many AFCIs can catch them? Only the ones that have GFP.
And to say such errors are to rare to justify GFP is an understatement. Since the inception of AFCIs countless wiring errors have been detected. In fact many AFCI reps will tell you close to 90% of AFCI nuisance tripping is the result GFP catching ground faults/wiring errors.
That is an issue I need to address.
Surely you don't believe the CMP should ignore this issue?
Firstly I represent a manufacturer (not of AFCI's) and our products are produced in accordance with UL standards. We do not shoot to exceed the standards, we shoot to meet the standards...
I do not blame manufactures, I blame the CMP. In the end it is them that have all the power.
AFCI technology speaking...on the most basic level of ARC detection their are specific characteristics that are replicable, modeled and perfectly acceptable to be used as foundation points in arc detection. The research that takes place are indeed now days done on finished product. However, continued research is constantly being done by the manufacturers to enhance the AFCI Technology because the manufacturing business is also a game of who gets it to market first and who enhances it to over shadow the competition, trust me (or not, thats your choice) every day manufacturers are trying to enhance and one-up the competition if only to say our product beats your product and NEMA, the collective body, can't restrict that competition.
I trust you. But that isn't stopping nuisance tripping from UL listed appliances.
When looking at the merits of a "premature" ...
And that's a half truth escape.
When one introduces an unreliable technology it back fires. There are and have been wonderful technologies with wonderful promises, but relying on them full scale is/was not economical even dangerous. Do you want a nuclear reactors built without all the safety bugs ironed out because said reactor will save some money on coal? I think not.
Same goes for AFCIs. When they are tripping on UL listed devices they get taken out. They force electricians to loose faith in the CMP, it forces an underground market of violating code.
I can see you making the argument "well, that is their decision not ours" And that may be true, but that simple defense does not changing a complex reality.
I believe the problem originally was that AFCI's were touted as the Holy Grail and when random issues came to light (even if installer error) it tainted that statement made by various manufacturers or invested advocates but it does not diminish the technology and advancements in terms of arc detection at least in my less than intelligent mind.
AFCI technology when done right is a layer of safety, but it needs improving.
But ultimately, the biggest contributor of electrical fires is not arcs, its glowing connections. Why is it that in 2015 no device or code mandate exists for every connection to have a device capable of shutting down the circuit when a glowing connection arises?
I personally believe that the largest hurdle...
And that is why CMP should not have mandated AFCIs until this was fixed. At this point a customer is nothing more than a research lab. AFCI will be swapped until the right on is found or they will all be failed, removed, and replaced with a regular breaker. How is that different than R&D?
Again, if the logic was amped up, it would get easier to differentiate between everything.