So you would do an improper installation just to get paid?Originally posted by joek:
Roger, the point is - do it the inspector's way, get the ticket signed off, get paid, and get out of there. The next time you do a similar job, first call the inspector.
Remember, sometimes the bear bites you, sometimes you bite the bear.
Do these townships have formal amendments for these requirements, or is it just somebodies whim?Re: Panel Wiring - There are townships in my area which requires the neutural and grounding wires be installed on separate bars. Some go as far as requiring the bare copper wire be wrapped in green tape.
This may be required in your area, and may be a good idea, but it is not required by the NEC.Re: Surge Protector - Since the nursing home has sensitive monitoring and life support systems, they must be protected from electrical surges when the generator comes on. This is required in my area.
The critical branch can not serve the F/A or any Alarm and Alerting Systems see 517.42(C) and 517.43.Re: Conduit wiring - You did not mention if the lighting conductors are for general or essential wiring. Also the critical wiring serves the fire alarm system and emergency call alarms. If the fire alarm system is power-limited you need to check 760.55 for cable separations.
Just to be clear you are talking about a service panel that includes the service disconnect?Originally posted by joek:
Depending on how the bonding is done (how the ground bar is connected to the neutral bar) That might be a problem with neutral wires on the ground bar.Originally posted by ccha9219:
He failed the main service because the grds and ntrl on the same bus bar
(he made us move the green wires to ground bar
and the white wires to the nut. bar )
While 250.118 lets us use the steel of an enclosure for grounding (not normally carrying current) I do not see any article that allows using the steel of an enclosure as a conductor that normally carries current as a neutral does.110.5 Conductors.
Conductors normally used to carry current shall be of copper unless otherwise provided in this Code. Where the conductor material is not specified, the material and the sizes given in this Code shall apply to copper conductors. Where other materials are used, the size shall be changed accordingly.