AHU's with built in breakers

Status
Not open for further replies.

ctmike

Senior Member
Would you consider the breakers that are installed on some AHU (air handling unit ) as a means of disconnect
?
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
Would you consider the breakers that are installed on some AHU (air handling unit ) as a means of disconnect
?

Yes. Can't remember the article but I believe it says "mounted on or a part of"
 

kwired

Electron manager
Location
NE Nebraska
Would you consider the breakers that are installed on some AHU (air handling unit ) as a means of disconnect
?

I have always considered that to be the main reason they are there in the first place.

They are certainly not needed for overcurrent protection most of the time.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
I have a fairly new unit and on the air handler there is a breaker. There is a label above the breaker that states it is only a means of disconnect and not OCPD.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
That means it is not a breaker, it is a molded case switch.

I suppose, but it is an actual breaker. The label actually says " Circuit breaker is not intended for branch circuit protection. It serves as a disconnect only."
I know what you mean but you could remove the breaker and install it in a panel and it would work as an OCPD.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Allow me to muddy the water a bit :D
Some of the AHUs I have inspected have a plastic cover over the
breaker/disconnects you reference. The cover is held closed by a screw.
Is this an acceptable disconnecting means ?
 

Billybob1

Member
Location
Oklahoma
AHU's with built in breakers

I have been told you can use the unit provided circuit breakers as the required disco, and I have been told you can't.

Never failed inspections useing them as a disco.

Reading 240.10 kinda gets me to thinking that it would be okay for disconnect but not for ocp.
 

kwired

Electron manager
Location
NE Nebraska
Allow me to muddy the water a bit :D
Some of the AHUs I have inspected have a plastic cover over the
breaker/disconnects you reference. The cover is held closed by a screw.
Is this an acceptable disconnecting means ?

If the branch circuit breaker is within sight but behind a panel door with a latch or lock it is still acceptable for same purpose so why not?
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Some of the AHUs I have inspected have a plastic cover over the breaker/disconnects you reference. The cover is held closed by a screw. Is this an acceptable disconnecting means ?
If the branch circuit breaker is within sight but behind a panel door with a latch or lock it is still acceptable for same purpose so why not?
My answer is yes to both. The disconnecting means is required to be "readily accessible." The definition of that phrase tells us that we have to be able to reach the disconnecting means quickly. But it does not tell us that we have to be able to operate it quickly (e.g., as an emergency shutoff).
 

Strife

Senior Member
The intent of "disconnect means within sight" is to be able to service a piece of equipment without some idiot turning the power on you.
Same reasons the on/of buttons on a range are allowed as means of disconnect(I know there's some additional requirements, so don't start).
Let's look at a connector/plug assembly. Been replacing 5-6 lately. Had to change the connector. Hey, where's MY means of disconnect. Personally I either have a helper stand by to make sure no one turns breaker on, or I take the panel cover off and take the wires off the breaker.

I have been told you can use the unit provided circuit breakers as the required disco, and I have been told you can't.

Never failed inspections useing them as a disco.

Reading 240.10 kinda gets me to thinking that it would be okay for disconnect but not for ocp.
 

highvolts582

Senior Member
Location
brick nj


My answer is yes to both. The disconnecting means is required to be "readily accessible." The definition of that phrase tells us that we have to be able to reach the disconnecting means quickly. But it does not tell us that we have to be able to operate it quickly (e.g., as an emergency shutoff).

I do not see how getting in an attic with a ladder is readily accessible yet the disconnect is always up there and never fails. within sight is what I go by.
 