Interesting, thanks for sharing. You sparked my curiosity and you're right - they do offer 120/240 3 Ph 4W up to 800A and even a 240V 3Ph 3W.
2. SERVICE SUPPLY VOLTAGES [...]
c. 240/120 VOLTS, 3-PHASE, 4-WIRE
(1) This voltage supplies single-phase and three-phase loads through the same metered service and
is normally limited to a service capacity of 800 amperes. Consult the Department when the
proposed service exceeds 800 amperes.
(2) The service neutral is center-tapped and grounded at the Department's transformer and the
"Power Leg" measures 208 volts-to-ground.
(3) Where service is supplied from dedicated transformers located on the customers premises, the
Department may require the service to be supplied with a four-wire wye voltage. See items 5 and
6.
d. 240 VOLTS, 3-PHASE, 3-WIRE
This voltage is generally not available for new services. New services may be permitted where an
existing premises is already supplied at this voltage. However, the customer is required to consult the
Department when planning increases in load or service ampacity to an existing service supplied at this
voltage. Such changes may require conversion to a 4-wire service.
Note: Single-phase loads connected to a 3∅ 3-wire service shall be reasonably balanced. The
customer’s system power factor (measured at the meter) shall not be less than 0.5 lagging.
http://www.kallin.com/ParkDrive/DWP Code.pdf
They don't actually say it is open delta but I have to imagine it is. If they had 3Ph distribution there would be no need to use a delta and you'd think they would offer you a 120/208 3Ph or 277/4703Ph 4W Wye.
I realize your drawing is preliminary but one thing to heed warning on is it looks like you are using the B phase for line neutral loads in the panelboard schedule. There will be a high leg at 208V to ground not 120V to ground. Utility will probably want you to land this on the C phase in their meter but downstream of that NEC will require it be the B phase. You will have to skip B phase for all single phase loads in the panelboard schedule and probably put warning sticker over each space so they don't install 1P breakers in B phase in the future.
That is too bad you have such high fault current. You're correct about 10kAIC standard. MFR's will offer 'high interrupting' 240V breakers probably only rated for 22kAIC. You will likely have to spec a panelboard for 277/480V system with breakers that have a 35kAIC rating at 480V and 65kAIC at 240V and pay that premium.