Most homes do not draw steady loads, even during the hottest days. Those AC units are cycling on and off, and at any given point in time (random snap shot) some ACs will be on and others will be off as they cycle relative to each other to maintain a set temperature. The same holds true for refrigerators, electric heat, even cooking during thanksgiving. So on a cool day that pole pig might only see 1/4 the AC units drawing current at any given point in time even if all of them are "on" (cycling) trying to maintain comfortable temperatures, and 1/2 to 2/3 current on a blistering hot day at any given point in time. Thus when everyone is away at work, the worse case assumption looks something like this:
1. 150-350 VA refrigerator (when the compartments are cold the compressor draw is actually a lot lower then the label. In fact sometimes the label is actually accounting the defrost heater(s) as a higher load x 125% or more %. Today's refrigerators are also more efficient for many regards, ie the case and door gasket heating is accomplished by running a portion of the condenser around the edge instead of a separate electric heater)
2. 150 VA Standby and miscellaneous loads (forgotten lights, charging electronics, appliance clocks, wifi, standby of TVs, game cubes, routers, printers, garage door opener, ect ect)
3. 2,500 VA exterior AC condensing unit (this will be higher or lower for many reasons even for the same ton units, but often less than 1/2 the MCA. Remember the MCA is already worse case x 125%)
4. 450 va air handler blower
So:
150VA x 11= 1,650 VA
450+2,500+150= 3,100 x 5.5 (since only half the units will be running at any point in time) = 17,050
= 18,700kVA on an August day with everyone at work
For a summer weekend with people home in between meals; vaccuming going on, some laundry, lights, TVs, game counciles, ect we might see 24kva. An extra electric clothes dryers or two could bump it up to 28kva for 15-20 minutes, then the heater cycles as the clothes loose mositure. A winter load (minus 2,500 VA ACs) would be 5,000 VA with 8,000VA in between meals when people are home.
So even during the hottest days the pig has sufficently reduced load and enough time to cool in between peak periods. If the stove and dryer are gas (I assumed they were both electric like some homes with a gas service) and there is good insulation in those walls, you could size that pig at 37.5kva. And yes, 37.5kva pigs do exist :thumbsup::
https://upload.wikimedia.org/wikiped...y_stepdown.jpg
If those hosues were all electric then I would say 4 homes would do it. Maybe 5 at 1200 sqft or good insulation. Worse case winter:
General: 150x4= 600
Refrigeration: 150x2= 300
8 VA pr square foot heating: 8 x 1,500 x 2 (assume half the heating is running at any given time)=24,000kva
So 24,900 kVA. 25kva is more then enough load relief to allow sufficient cooling ESPECIALLY in the dead of winter. Then we can do a 250% overload as people start to shower around the same time/ wash dishes/do laundry {4 water heaters @ 18.75 amps each = 18kVA}, crank up the electric heat, make toast, preheat the oven, skillet, laundry, lights, hair dryer, ect, ect.
Of note, I am aware that its often 10va per foot when calculated by the electrician, however, as you oversize electric heat the diversity increases. So instead of multiplying by two, we could do 1.8. Hence why I decided on 8va from the start- kept the two.