I have 2 200 amp main breaker panels in a medical building that are rated for 10k each and 2 200 amp non fused Disconnect that are rated for 10 k each. The inspector wants 22k AIC rating so my question is can i replace the disconnect breaker and leave the panels at 10k? The inspector is requisition amendment letter from the site engineer which in return he needs a letter from the power company which hasn't got back to yet. Try to figure out other Options before i start getting fine bye the GC
What is the inspector's request based upon? From what I can tell it's because he said so. Or, what he customarily has seen in similar facilitiesin the area. Not good enough.
Ask you POCO first. If not, plan B is to identify the KVA of the transformer which feeds your facility to determine we ith a we ordered posible case sinerio using an unlimited fault current available from you POCO and a 100% motor contribution.
If that figure exceeds 10ka then start fine tuning the results with a fault systems study done by a PE who has experience to do how much dodo you are in. They have the wherewithal to do any calculations that are necessaru to determine the actual available fault current at the secondary of you transformer as well as all the conductor and other components rhat may contribute to the system nimpedance to reduce the available fault current as well as any devices that my contribute to it.
If you do discover a problem you may want to consider if any of the over current protective devices can be series rated with an upstream overcurrent protective device that will allow those down stream devices to be series rated.
You have to first with the facts and not because he said so. You may very well have an issue. But, if you have to make adjustments it would be prudent to do and upgrade as cost effectively as possible.