Bryan,
It depends on whether the system is specified by the designer as fully rated or series rated.
If the calculated SCCR is 19,000A at the line side of the service disconnecting means, then the main and branches can be rated at 22kAIC; or the main and branch can be any rating as long as the manufacturer has a series rating for them at 22kAIC (so individually they might be main=22kAIC and branch=10kAIC).
If the SCCR is 9,000A and specified to be fully rated at 22kAIC, then the main and branch must be 22kAIC. They could also have a series rating to meet the 22kAIC requirement of the designer, where the branch might be 10kAIC.
It depends on whether the system is specified by the designer as fully rated or series rated.
If the calculated SCCR is 19,000A at the line side of the service disconnecting means, then the main and branches can be rated at 22kAIC; or the main and branch can be any rating as long as the manufacturer has a series rating for them at 22kAIC (so individually they might be main=22kAIC and branch=10kAIC).
If the SCCR is 9,000A and specified to be fully rated at 22kAIC, then the main and branch must be 22kAIC. They could also have a series rating to meet the 22kAIC requirement of the designer, where the branch might be 10kAIC.