Because since 1973 I have been thinking that 10 wire needs to be protected by a 30 amp breaker.
I come her to try and learn and I just get reminded that I obviously don't understand anything.
Don't give up, hang out here.
A while back I would have felt as surprised as you that 10 AWG may be on a larger breaker.
Normally a breaker or fuse is installed to provide both
overload and short circuit protection.
With a motor circuit things change, the breaker or fuse is only installed for short circuit and ground fault protection.
If there is a short circuit (Line to line direct connection) or a Ground fault (line to ground direct connection) the 60 amp breaker will open quick enough so the 10 AWG will not be damaged.
As an example, have you ever run a 60 amp feeder?
What size EGC would you run?
The code requires a 10 AWG, if there is a ground fault that 10 AWG will be large enough to open the 60 amp breaker.
Short circuits are very different then overload, overload is another issue all together.
The only way for motor circuit conductors to be overloaded is if the motor starts to malfunction.
So by installing the code required motor overload protection we also end up protecting the conductors for overload.
If the motor draws to much current the motor overloads will open stopping the overload condition