Stackers instead of a bit larger staple? How about them new GEC box connectors that I can't remember the name right at the moment?
Last edited:
So in conclusion : We have a wire manufacturer that says it is not required, the Lug listing from the panelboard manufacturer says it is not required, but I have an inspector who "thinks" that it is required, and a very big portion of the electrical community that uses it regardless.
Why can't I come up with a product that is not needed but everyone still buys it !!!!
How about them new GEC box connectors that I can't remember the name right at the moment?
Had an inspection on temp service today in an area I don't typically work in. Inspector said I failed due to the terminations of the AL conductors lacking an antioxidant compound ?
I of coarse ask what article I had violated ? His reply was 110.14.
My argument is the lugs are rated for AL, nowhere in 110.14 does it say I have to use an antioxidant. Nor does it say if I use an antioxidant it is ok to mix AL on non rated rated lugs. I don't see that its use is a requirement at all. I was always under the impression antioxidant was to prevent or reduce oxidation from the air, it has no effect on corrosion due to dissimilar metals.
Further my understanding is with the new AL conductors, they are alloy anyways and it is not required.
He didn't give me a red tag, but didn't give me a green one either - he said he would call me on Monday. So am I wrong on this ?
I've watched the POCO guys here make up the line side in a meter base. They squeeze out a dollop about the size of a green pea in the back of the terminal, lay the conductor on top of it, install the top of the terminal, and crank it down.Not in the code, but in my area of pennsylvania the POCO requires it. All Alum. conductor terminations at the service.
I've watched the POCO guys here make up the line side in a meter base. They squeeze out a dollop about the size of a green pea in the back of the terminal, lay the conductor on top of it, install the top of the terminal, and crank it down.
I always coat the exposed strands, but I don't wire-brush it in. I also uncrew the lug screws and put a little no-ox on the threads, both in meter bases and main breakers and lugs.
Well I did get a return call this morning from the inspector saying he had some "mis - information"... That he would release to POCO today :roll:
At least he is willing to admit he had "mis-information" and released the temp to the POCO.
Chris
Take a look at some 30 year old Al connections on service feeders into panels, especially in humid areas. Then you'll see why the inspector wants it.
Pretty cheap protection,
and you'll keep the local AHJ happy
I've found that you need to check the torque on Al wire connections periodically and add more anti-ox as needed. The thermal expansion contraction compared to Cu can loosen the connection over time.
“He who tightens threaded aluminum without no-ox figures someone else will have to deal with it in the future.”