I think people are finally waking up, but still the myth of grounding electrodes clearing breakers persists:
https://youtu.be/LoQVdEQlmXM?t=380
Ground rods are NOT a backup EGCs, service neutral, or effective ground fault current path, and have nothing to do with fault clearing even if the service neutral is lost. Yes metal water mains might, but that is not the intent of the NEC or the intent of grounding electrodes.