Wiring my cousin's house...a family deal....low cost and save a buck if I can.
Yesterday I set the Meter Can and directly inside (back to back), I mounted a 200A Main Breaker panel.
Out of Meter, thru close nipple and into Panel.
Looking thru my wire scrap, I found a 6' piece of Southwire USE-2 "Alumaflex" Mobile Home Feeder Cable, 4/0,4/0,2/0,#2 (cross rated RHH, RHW).
I discarded the #2 grounding conductor, and use the remaining three conductors for the Service entrance.
This particular cable is very soft and easy to bend.
That and the cross rating makes it ideal for service cable, especially if you're entering the dwelling with it.
I also used N0-lox on the terminations and worked it into the strands with a wire brush.
I know one particular inspector that will fail a installation if he can't see brush marks where the Anti-oxidant has been applied.
It's required where I am, and standard procedure for me.:smile:
That and using a torque wrench to tighten the terminals.
I always remove the set screws on the terminals and coat them with anti-oxidant too.
I had a bad experience one time with a terminal set screw that had oxidized, and caused me to have a customers electrical service disconnected for about 4 hours longer than I (and she) had planned..
steve