Always test power after you pull the meter.

Status
Not open for further replies.

220/221

Senior Member
Location
AZ
I have a habit of ALWAYS testing for power, even after the meter is pulled.

Today, that habit paid off.

electrical200.jpg


I have seen this meter can a hundred times but this one had test blocks built in.

I didn't see them at first, I just noticed that there was bus behind the meter jaws connecting line and load. Each leg had a brown insulated thing sticking out under the top jaws and when the meter was pushed it, it disconnected the bus jumpers.

electrical202.jpg
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Looks like a lovely place to work. A Zinsco panel on the left and a FPE on the right.
Is doesn't get much better than that.:D
 

ultramegabob

Senior Member
Location
Indiana
Hey great catch on that one, that could have been a real bad day for you if you had not taken a minute to check, thanks for the heads up!
 

mivey

Senior Member
Great habit!

Double check everything. Equipment fails.

Don't trust the self shorting equipment to work. Some meters with the CT self-shorting devices may have a failure due to dirt, bugs, corrosion, etc and the CT secondary will be left open.
 