I mean could i read amps from all three phases on the neutral inside the panel?

The nominal current on any the neutral is the unbalanced current of the loads it supplies. Any current other than that is a from leakage or fault condition.
 
If you are reading significant current (10-30% or more) of the load on the neutral, there is a probability that something th the system is causing harmonics. If a large percentage of the load on the panel is non-linear (drives, other items with switching power supplies, especially single phase) harmonics can be a significant issue.

Good Luck!
 
If you are reading significant current (10-30% or more) of the load on the neutral, there is a probability that something th the system is causing harmonics. If a large percentage of the load on the panel is non-linear (drives, other items with switching power supplies, especially single phase) harmonics can be a significant issue.

Good Luck!
But only on a three phase system. The harmonics do not cause increased neutral current on single phase systems.
 
Just hall can lites 3 tube ballast - hall recpts- and 4 bathroom fan lite heat combos using around 25 cks in panel but there are alot of neutral shareing going on
 
The nominal current on any the neutral is the unbalanced current of the loads it supplies. Any current other than that is a from leakage or fault condition.

Actually you will seldom have leakage current on the neutral generally this is on the ground, fault current should be for a short duration for a phase to neutral fault, that is till the OCP operates to clear the fault.
 
If you are reading significant current (10-30% or more) of the load on the neutral, there is a probability that something th the system is causing harmonics. If a large percentage of the load on the panel is non-linear (drives, other items with switching power supplies, especially single phase) harmonics can be a significant issue.

Good Luck!

And this is not necessarily true. DEPENDS ON the load in the panel and how well they are balanced. Few drives are single phase and will not contributer to the neutral current.

If you cannot find the problem you have overlooked the problem. This should be one of 3 maybe 4 things all noted above (that I can think of). RECHECK EVERYTHING
 
Last edited:
That would be true for single phase 120/ 240.
Some considerations should be made for 120/208 and other three phase WYE systems.
It is true for any neutral conductor, it carries [under normal operating conditions] the unbalanced current only, period. And that even includes harmonics, as that current is also unbalanced. Doesn't matter if its single phase, split phase, or three phase.
 