Yes, assuming the load is not perfectly balanced.Should you be able to put a amp probe on the neutral from swithch gear inside the panel and read AMPS?
three phase 120- 208
I mean could i read amps from all three phases on the neutral inside the panel?
But only on a three phase system. The harmonics do not cause increased neutral current on single phase systems.If you are reading significant current (10-30% or more) of the load on the neutral, there is a probability that something th the system is causing harmonics. If a large percentage of the load on the panel is non-linear (drives, other items with switching power supplies, especially single phase) harmonics can be a significant issue.
Good Luck!
Yes, when the current is greater than the ampacity of the conductor.Are we talking about a big # if panel is is full demand? Is there a point when a RED FLAG should be waived?
The nominal current on any the neutral is the unbalanced current of the loads it supplies. Any current other than that is a from leakage or fault condition.
Good Luck!
It is true for any neutral conductor, it carries [under normal operating conditions] the unbalanced current only, period. And that even includes harmonics, as that current is also unbalanced. Doesn't matter if its single phase, split phase, or three phase.That would be true for single phase 120/ 240.
Some considerations should be made for 120/208 and other three phase WYE systems.