IMHO all cases of signature based nuisance tripping of AFCIs (which by definition do not involve the GF detection component) are false series arc detections. Unlike parallel arc detection, a series arc signature trip only requires about 8A of current through the breaker.
On the other hand RF induced malfunctions of the electronics could affect a breaker even with zero current.