250.26 Conductor to Be Grounded ? Alternating-Current Systems.
For ac premises wiring systems, the conductor to be grounded shall be as specified in the following:
(1) Single-phase, 2-wire ? one conductor
(2) Single-phase, 3-wire ? the neutral conductor
Where is the exception for portable generators?
225.32 Location.
The disconnecting means shall be installed either inside or outside of the building or structure served or where the conductors pass through the building or structure. The disconnecting means shall be at a readily accessible location nearest the point of entrance of the conductors.
Again no exception for portable generators and we can even find more information concerning this here
702.12 Outdoor Generator Sets.
Where an outdoor housed generator set is equipped with a readily accessible disconnecting means located within sight of the building or structure supplied, an additional disconnecting means shall not be required where ungrounded conductors serve or pass through the building or structure. The disconnecting means shall meet the requirements of
225.36.
And this is what 225.36 has to say
225.36 Suitable for Service Equipment.
The disconnecting means specified in
225.31 shall be suitable for use as service equipment.
You and golddigger are both mistaken about the bonding in the service panel clearing a fault with the generator unless the generator is bonded to the neutral for the other devices located on the generator.
In 250.34 there are three different types of generators being talked about.
- Portable with receptacle mounted on the frame
- Vehicle mounted generators with receptacle mounted on the frame
- Generators that don?t have receptacles mounted on the frame
The informational note applies to the entire section not just (C) as there would be no need for it to address C now would there.
Once the generator is connected to the premises wiring then it must comply with 250.30 which addresses which type of system?
I'm curious;
What is your response if you show up for the final and there is an interlock connected to an outside power inlet with your required service rated disconnect - but, no generator on-site, or in sight?
(Inspector) What's this for?
(Journeyman - or in my case of DIY to the max - me) Eventually they will get a generator - can't afford one right now. That is for the future connection.
(I) You have to have a 3W transfer switch and install it as an SDS.
(J) Owner tells me he is going to get a code compliant gen and install as a non-SDS.
What are you going to do? Tell the owner he is lying and to rip out the circuit?
With utmost respect, your not liking it does not make it unsafe or illegal.
I will point out the code sections outlined above and reject the installation as any other code official would do if they are doing the job they have sworn to do.