Since I haven't done this in awhile, correct me if I'm wrong (and thus reeducate me): A pool subpanel requires a four wire install and a ground rod. Or two. ?
The pool I did last year I needed two rods.Since I haven't done this in awhile, correct me if I'm wrong (and thus reeducate me): A pool subpanel requires a four wire install and a ground rod. Or two. ?
No concrete answer,
680.25 provides the details on a feeder to a pool panel. If you are supplying 240/120 it would be 4 wire as an equipment grounding conductor is required for the feeder.
As far as the ground rod, a pool panel installed in/on the same structure as the service would not require a ground rod (or any grounding other than required by 680.25) If the pool panel is on or in itself a separate structure the 250.30 would require a grounding electrode system at the separate structure.
There is no ground rod requirement associated with a pool install as far as the pool is concerned..
Whether or not a ground rod is necessary has nothing to do with the presence of a pool. A rod may not even be needed even in a separate building or structure either. What is required at separate structures is a grounding electrode system. If no natural electrodes are present you can use a made electrode and a ground rod is usually the electrode of choice as it is usually the simplest and least expensive made electrode to install.Thanks very much. But, you know, an inground pool is, in fact, a separate structure. "Contrariwise..., if it isn't, it ain't; that's logic." And I understand that but, in this case it IS.
Crazy question but are you sure this whole equipotential thing makes any sense at all? They're essentially saying DON'T drive a ground rod here. But make sure you drive one over there because that other separate structure (like a garage for instance) is made out of concrete and wood and, etc. (?) I don't really need an explanation of gradients; I just need to know if this makes any realistic practical sense.
Thanks very much. But, you know, an inground pool is, in fact, a separate structure. "Contrariwise..., if it isn't, it ain't; that's logic." And I understand that but, in this case it IS.
Crazy question but are you sure this whole equipotential thing makes any sense at all? They're essentially saying DON'T drive a ground rod here. But make sure you drive one over there because that other separate structure (like a garage for instance) is made out of concrete and wood and, etc. (?) I don't really need an explanation of gradients; I just need to know if this makes any realistic practical sense.
Since I haven't done this in awhile, correct me if I'm wrong (and thus reeducate me): A pool subpanel requires a four wire install and a ground rod. Or two. ?
you know, an inground pool is, in fact, a separate structure. "Contrariwise..., if it isn't, it ain't; that's logic." And I understand that but, in this case it IS.
Crazy question but are you sure this whole equipotential thing makes any sense at all? They're essentially saying DON'T drive a ground rod here. But make sure you drive one over there because that other separate structure (like a garage for instance) is made out of concrete and wood and, etc. (?) I don't really need an explanation of gradients; I just need to know if this makes any realistic practical sense.
The use of the ground rod is not necessary to a sub panel connected on the building. The idea is that the initial install of the grounding electrode conductor should protect from surges etc. When a panel is remotely located the surge at that location will not be protected by the service grounding electrode conductor. That is my guess as to why we need a grounding electrode at the remote panel.
The grounding electrode is not there to protect people in the pool.
Is it fair to say that NEC use of the term structure is in effort to correspond to, and align with, building codes? And we all know why they use the term structure, right?
Be that as it may, I fail to see any significant difference between the subpanel that supplies a swimming pool and the subpanel that supplies, say, a residential garage. They are both structures distantly located that require power. So why a ground rod at one location and not the other? Wouldn't it be fair to say, here, that "truth" (or theory) requires consistency?
You're asking me if it is more important that I be right or more important that I conform and to me the answer is very obvious. We've been screwing up pool installations now for at least 40 years. I know; I was there. The primary issue is safety; do you mean to tell me that with all of our advanced technology there isn't a better way to ensure bathers are not lit up? The equipotential grid really doesn't make any sense if we fail to go that one, last extra mile. And simply providing a metallic gradient-free zone for what reason, stray voltages? does not make sense.
If it is required at a remote structure to place all bonded at earth potential, then it is required at a pool subpanel which is also a remote structure.
I don't believe the code makes this exception. Again, though, it becomes a question of when do things make sense. Does it make sense to make an exception for parking lot lighting? No. But at least this one is specified with the words single branch ckt.
Again I would have to question if any of this separate "equipotential" stuff makes sense.
NEC use of the term structure is not necessarily all that clear, it is something that seems to be questioned a lot. "Structure" may be relatively clear, but "separate structure" is not always all that clear. You may have two items that individually qualify as a structure, but if they are somehow connected to one another they may or may not be considered "separate structures"Is it fair to say that NEC use of the term structure is in effort to correspond to, and align with, building codes? And we all know why they use the term structure, right?
Like I mentioned just above - a "ground rod" may not be needed at the separate structure whether it is a garage or a pool. A concrete encased electrode would be required to be used as a grounding electrode at the separate structure if it exists. If a CEE is used a ground rod would not be required - typically the CEE will have much lower resistance than a rod will ever have is main reason why.Be that as it may, I fail to see any significant difference between the subpanel that supplies a swimming pool and the subpanel that supplies, say, a residential garage. They are both structures distantly located that require power. So why a ground rod at one location and not the other? Wouldn't it be fair to say, here, that "truth" (or theory) requires consistency?
This is where you need to understand the different purpose served by the grounding electrode and the equipotential bonding system. They are not installed for the same reasons and have different properties they bring to the installation. The two are bonded to one another or possibly one is a part of the other, but you have two different concerns with each application.You're asking me if it is more important that I be right or more important that I conform and to me the answer is very obvious. We've been screwing up pool installations now for at least 40 years. I know; I was there. The primary issue is safety; do you mean to tell me that with all of our advanced technology there isn't a better way to ensure bathers are not lit up? The equipotential grid really doesn't make any sense if we fail to go that one, last extra mile. And simply providing a metallic gradient-free zone for what reason, stray voltages? does not make sense.
The use of the ground rod is not necessary to a sub panel connected on the building. The idea is that the initial install of the grounding electrode conductor should protect from surges etc. When a panel is remotely located the surge at that location will not be protected by the service grounding electrode conductor. That is my guess as to why we need a grounding electrode at the remote panel.
The grounding electrode is not there to protect people in the pool.
Thought it was clarified earlier. 250.32 requires a grounding electrode for the panel at a separate structure (it does not require one for a single or multiwire branch circuit).I think you're missing the point: both the pool and the separate building are structures. If it is necessary at one, then it is necessary at the other.