Well for not saying much more you sure covered a good bit of spacejwelectric said:Well I don?t guess there is much need to say much more.
You're quite welcome, FWIW. I'm just sorry we cannot reach a mutual understanding.Well I sure do appreciate you running around helping me find my way but I think that I will jerk free for a while and let someone help me with this one, mightily feared that you might be headed the wrong way.
Well, no. Not explicitly. Either one see's the connection or they don't. Apparently you don't. Sometimes one has to visualize beyond the written word, and even go as far as to integrate concepts to obtain a better understanding of it all. Some say its all in the details. But in complex mechanics, if the details don't coalesce, they are proven to be meaningless.I would like to ask why you see a need to compare Busways to Panels? Surely you are not trying to use the rules for Busways for panels are you?
Per my last response, consider the jaunt retracted. As for 408 and 408.36(A), I in no way said the wording is unclear. I did say in effect though that the means of overcurrent protection required in the exception is not specific. Unclear, not specific... unclear, not specific... not the same meaning in my book.I stand my ground. I just can?t agree with what you are saying because of how it reads.
First you refer to a section of the code that allows 240.21 in an exception. No such exception exists in 408 and 408.36(A) is clear about the feeders in the first exception.
Now let's expand a little on the scope of that exception, specifically "if the panelboard feeder has overcurrent protection not greater than the rating of the panelboard." Can we agree the #6 conductors are the panelboard feeder? Assuming a yes, we follow them to their supply end to find they are connected to busbars having greater ampacity and overcurrent protection. The panelboard feeder seems to meet the definition of tap conductors. We look up tap conductors and find their are defined in what article? Oh... that would be Article 240 ? Overcurrent Protection. The first occurence therein is under 240.2 Definitions and we confirm the panelboard feeder is in fact tap conductors. The next occurence is in 240.4 Protection of Conductors, (E) Tap Conductors, which states, "Tap conductors shall be permitted to be protected against overcurrent in accordance with the following:" and lists six items. Since we are dealing with a panelboard feeder we find it in "(5) 368.17(C) Feeder or Branch Circuits (busway taps)"...
Now you should be able to make the connection I mentioned earlier. That connection leads us back to 240.21(B) and the rest is current history