Battery Energy Storage Systems (BESS) ready. All single-family residences that include one or two dwelling units, which a load-serving entity provides with electrical service for the dwelling unit that is greater than 125 amps, shall meet the following.
(1) At least one of the following shall be provided:
(A) BESS-ready interconnection equipment with a minimum backed-up capacity of 60 amps and a minimum of four BESS-supplied branch circuits specified in Section 150.0(s)2, or
(B) A dedicated raceway from the main service to a panelboard (subpanel) that supplies the branch circuits in Section 150.0(s)2. All branch circuits are permitted to be supplied by the main service panel prior to the installation of a BESS. The trade size of the raceway shall be not less than 1 inch. The panelboard that supplies the branch circuits (subpanel) must be labeled "Subpanel shall include all backed-up load circuits."
(2) A minimum of four branch circuits shall be identified and have their source of supply collocated at a single panelboard suitable to be supplied by the BESS. At least one circuit shall supply the refrigerator, one lighting circuit shall be located near the primary egress and at least one circuit shall supply a sleeping room receptacle outlet.
(3) The main panelboard shall have a minimum busbar rating of 225 amps.
(4) Sufficient space shall be reserved to allow future installation of a system isolation equipment/transfer switch within 3 feet of the main panelboard. Raceways shall be installed between the panelboard and the system isolation equipment/transfer switch location to allow the connection of backup power source.
Exception to Section 150.0(s): Buildings which have a BESS installed.