Does there exist an approved coating for aluminum conduit to pass through a concrete deck, subject to moisture?
Although the code seems to allow it "in theory" [344.10 (B) (2)], I can't seem to find an approved product.
Thoughts anyone?

Thanks!
 
Does there exist an approved coating for aluminum conduit to pass through a concrete deck, subject to moisture?
Although the code seems to allow it "in theory" [344.10 (B) (2)], I can't seem to find an approved product.
Thoughts anyone?

Thanks!

PVC sleeve.
 
PVC coated conduit, compounds, and tape wraps and shrink wrap may all be acceptable. Sounds to me like its just the AHJ's call;

Can't get the link to work: Just do a search for NEMA Bulletin UL and NEC Requirements for Corrosion Protection of Galvanized Steel Conduit and Electrical Metallic Conduit

It also talks about aluminium conduit.

The Aluminium Association also has good info. in a PDF. Search for the Aluminium Association Chapter 17 - Rigid Aluminum conduit (they actually have it misspelled as Conduct but I think you'll find it).

Allied Tube and Conduit lists bitumastic paint as a paint approved for the purpose.
 
Last edited:
Pipe wrap is pretty readily available. Like the others mentioned though, there are other methods. It would be worth a few minutes of your time to consult with your AHJ.
 
My interpretation is that there is no actual "approved product" and whatever you decide to use must be approved by the AHJ. That's your approval.

That said, I second the PVC sleeve method, but get approval from the AHJ first.

-Hal
 