rdixon said:Do receptacles for lighting loads have to be arch fault protected in dwellings?
According to his zip code, Hilliard, FL. :smile:celtic said:. . . So, where are you?
charlie said:According to his zip code, Hilliard, FL. :smile:
Isn't that shown at the bottom of his public profile? It is not my intention to reveal private information. :-?celtic said:TY charlie....that's a mod-only feature.
charlie said:Isn't that shown at the bottom of his public profile? It is not my intention to reveal private information. :-?
To more fully reply to your question. All the outlets on the circuit have to be arc fault protected, this includes lighting outlets. An inspector that tells you that a lighting outlet is to be protected is correct. Also, the entire circuit shall also be protected.![]()
"210.12(B) Dwelling Units. All 120-volt, single phase, 15- and 20-ampere branch circuits supplying outlets installed in dwelling unit family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation rooms, closets, hallways, or similar rooms or areas shall be protected by a listed arc-fault circuit interrupter, combination-type, installed to provide protection of the branch circuit."
Would this also apply to 120 volt smoke detectors installed in the bedroom and connected to the other detectors?
210.12... i consider anything inside the bedroom as being required to be on arc faults. i also consider the bedroom closet as part of this. right or wrong?
thanks
210.12(B) 2008 requires closets, too.
sorry should have clairified this permit was pulled in 2007
Why not kitchen lights?We arc fault everything except...furnace, fridge, kitchen lights and all 20 amp GFI protected circuits (Kitchen plugs, Bath, etc...)
Absolutely.
Boatfull, I think a closet accessed from and associated with a bedroom is a part of that bedroom. That's just me though. :smile: