pistolpigg
- cookeville,tn
Are arc flash calculations based on worst case scenarios as I assume. For example motors or loads running or connected at time of for example disconnect?
If a motor load is removed by for example by a starter and there is no way to add resistance to a circuit for example operating a disconnect after a stop is applied then wouldn't the possibility of an arc be almost nonexistent because of no resistance?
Wouldn' t a motor or circuit being turned off lower arc flash cal and possibly ppe and could this be put on the arc flash notification stickers?
I'm trying to figure out why and how it would logical to have to put a hrc four requirement to operate a disconnect for a motor when its load is disconnected by a motor starter or a drive. Seems like a lot of overkill for operating a device that has no load for example.
Incident energy calculations are not intended to include any factor of risk or probability. To use your analogy, the calculations only give you the payout not the odds.Ok that makes sense about the clearing time and the arc flash calculation but the thing that seems to be missing from all the arc flash calculation is probability of an event in relation to the task performed. In other words would it be a good comparison to buying a lottery ticket ?
So do most places require the ppe on the arc flash sticker for operation of disconnects and verification of no power with a meter to get it to a safe work position?
Many companies have developed their own safe work practices addressing the operation of disconnects and circuit breakers which accomodate the Informational Note #1 to the definition of Arc Flash Hazard in NFPA70E-2012 and include some risk assessment.So do most places require the ppe on the arc flash sticker for operation of disconnects and verification of no power with a meter to get it to a safe work position?
Going back to original question then should we not factor in probability in when the chance of something happening such as an arc flash incident during non contact procedures such as operation of a disconnect or Mcc bucket with power off and or load disconnected? Seems like trying to drive a nail with a sledge hammer to me.
I know of no company with a safe work practice that does not consider 'verification of no power' as one of the riskiest tasks that can be performed and therefore requires the use of the 'worst case' PPE.