That's a curious statement.
Loose connections cause arcing, no?
Not always. An undertorqued termination will overheat without arcing.
They might, but in many cases they just create heat...the glowing connection is not an arc, but produces enough heat to cause the wire and termination to actually glow red.That's a curious statement.
GCI - Glow-fault Circuit InterrupterGlowing Fault Circuit Interrupter
There was a proposed device that had a thermal element that when exposed to too much heat, created a ground fault using a resistor to limit the ground fault current to 30mA or so, and to be used along with a GFCI. When the poor connection caused too much heat, it shorted to ground causing the GFCI to trip. I think it was proposed as a code requirement 3 or 4 cycles ago.Since AFCI breakers don't recognize glowing connections, I'm going to invent GFCI
May have to change the name slightly as we already have GFCI
= Glowing Fault Circuit Interrupter
GCCI
Glowing Connection Circuit Interrupter!![]()
Would that be inside of each box or each device or what was the details of the idea?There was a proposed device that had a thermal element that when exposed to too much heat, created a ground fault using a resistor to limit the ground fault current to 30mA or so, and to be used along with a GFCI. When the poor connection caused too much heat, it shorted to ground causing the GFCI to trip. I think it was proposed as a code requirement 3 or 4 cycles ago.
Yes, you would install one at each device and possibly at junction boxes too.Would that be inside of each box or each device or what was the details of the idea?
Good idea but man that's some serious money. Standard track house Gfpe breaker +2000 bucks + 3 bucks for each box so +400 for the house then once in the code price doubles because they don't make enough stock for them so more like 4800 bucks extra in stuff not to mention box fill.Yes, you would install one at each device and possibly at junction boxes too.
Standard GFCI breakers for each circuit and many circuits already require GFCI protection.Good idea but man that's some serious money. Standard track house Gfpe breaker +2000 bucks + 3 bucks for each box so +400 for the house then once in the code price doubles because they don't make enough stock for them so more like 4800 bucks extra in stuff not to mention box fill.
"This product is not intended to diagnose, treat, cure, or prevent any disease."
So would this have been included with normal gfci devices then. Was that the manufacturer suggestion. If gfci breakers were always required that'd be full space breakers only essentially then.Standard GFCI breakers for each circuit and many circuits already require GFCI protection.
Trips on GFCI breaker, but not line-fed GFCI outletsSo, what happens if the neutrals get crossed at down stream junction boxes ?
Then use SQ-D and Siemens, which always had 30mA ground fault function in AFCI's.I would choose a GFCI breaker or Dual Function breaker over and AFCI breaker
Not if trouble occurs before the GFCI, which is line-side blind.There is a much better chance of a glowing connection ..tripping the GFCI than an AFCI
I believe 120/240v AFCI's trip from noise in all directions, including arcs per UL1699 standard.(Arcs) is what AFCIs are supposed to detect and protect against.
Plug on neutral siemens and the siemens tandem now don't have gfpe in themThen use SQ-D and Siemens, which always had 30mA ground fault function in AFCI's.
But this thread is about protecting AL branch circuit wiring with AFCI breakers.Not if trouble occurs before the GFCI, which is line-side blind.
Yep, Square D seems to be the only one to still included it. Eaton CH might but I have not checked recently.Plug on neutral siemens and the siemens tandem now don't have gfpe in them