I have no problem with them asking the POCO to move the drop, but would have a problem if they fail my inspection over something I had no control over. Like I said before if I am responsible for mounting the attachment point, I don't have a problem with failing the height of attachment point if it doesn't allow for proper clearances but do have a problem if the POCO leaves excess sag in the conductor that causes a clearance violation and they pin that on me.
It's kind of a strange situation. The EC doesn't get failed, rather the installation won't get approved if the drop on private property does not comply with the requirements in 230. If the EC physically can't locate a weather head so the drop is in compliance, then the inspector calls the POCO engineer and they meet to come up with a suitable solution. Sometimes it's just taking out sag, other times it's moving the drop from one side of the property to the other.
But, as iwire has pointed out, such practice is not covered in the NEC and may be part of our state rules. I suppose I should know that, having had to deal with it for so long.