5-31 Log #315 NEC-P05 Final Action: Accept in Principle
(200.2)
_______________________________________________________________
Submitter: Robert J. Walsh, City of Hayward
Recommendation: Revise text to read as follows:
All premises wiring systems, other than circuits and systems exempted or
prohibited by 210.10, 215.7, 250.21, 250.22, 250.162, 430.21, 430.25, 503.155,
517.63, 668.11, 668.21, and 690.41 Exception, shall have a grounded conductor
that is identified in accordance with 200.6. The grounded conductor shall
comply with 200.2(A) and (B).
Substantiation: Many loads do not require a neutral conductor such as electric
Motors.
Panel Meeting Action: Accept in Principle
Revise the existing text of the 2008 NEC to read:
“All premises wiring systems, other than circuits and systems specifically
exempted or prohibited by other sections of this Code 210.10, 215.7, 250.21,
250.22, 250.162, 503.155, 517.63, 668.11, 668.21, and 690.41, Exception, shall
have a grounded conductor that is identified in accordance with 200.6. The
grounded conductor shall comply with 200.2(A) and (B).”
This action does not affect the existing text of 200.2(A) and 200.2(B).
Panel Statement: CMP-5 recognizes there are other sections than those
included in the list or suggested text that are not required to have a grounded
conductor.
Number Eligible to Vote: 16
Ballot Results: Affirmative: 13 Negative: 3
Explanation of Negative:
DOBROWSKY, P.: This section should be deleted in its entirety. Modifying
the language is not incorrect but it is now essentially useless and provides no
guidance to the user. If a grounded conductor is required specific sections
already address that, stating that one is always required- unless specifically
exempted “somewhere” adds no value.
HARDING, G.: The panel action appears to only remove the list from this
requirement and does not address the actual concerns of the submitter. The
panel action should have included a new sentence to read as follows:
“For premises wiring systems, a grounded conductor shall not be required to
be installed with the ungrounded conductors of a feeder or branch circuit where
it is unnecessary based on the load served.”
WILLIAMS, D.: This proposal should be a straight accept. The present
section wording provides a number of sections where a grounded conductor is
not required to be routed with branch circuits or feeder applications. The
submitter has included two additional sections where a grounded conductor
should not be required for a motor branch circuits and feeders. Since it was not
referenced in this section a grounded conductor is required. The panels actions
of removing the listed sections will now require a grounded conductor routed
to all of the previously referenced sections unless specifically exempted in the
code.
Comment on Affirmative:
JOHNSTON, M.: Continue to accept the revisions as proposed as a proactive
approach in NEC development. The revision removes the list and results in a
reference that is more likely to remain accurate in subsequent NEC cycles. The
concerns of the submitter should be addressed by including clear text that
relaxes the requirement for a grounded conductor to be installed with all
circuits where it is unnecessary because of the type of load the circuit serves. A
three-phase load should not always be required to include a grounded (neutral)
conductor.