I seem to recall a couple of case studies with larger cable tray and high current circuits where the separation distance between the circuit conductors and the EGC was enough that the increased impedance of the EGC reduced the fault current from the instantaneous part of the OCPD to the short time part increasing the damage at the point of the fault as a result of the increased fault clearing time.
I don't have my green book handy but as I recall a 3' separation between the circuit conductors and the EGC doubles the impedance of the fault clearing path.
I don't have my green book handy but as I recall a 3' separation between the circuit conductors and the EGC doubles the impedance of the fault clearing path.