Article 450 Interpretation

Status
Not open for further replies.

FaradayFF

Senior Member
Location
California
Hi Guys,
Per Article 450, Table 450.3(B), does 1000Volts and less refer to the secondary voltage rating on the transformer? If my primary is selected properly per the table, then no secondary protection is required.

Thanks,
EE
 
Just a tip, if I look at just Table 450.3(B) I often can't remember whether it's referring to secondary, or both primary and secondary for the 1000V limit. So to "cheat" I just look at the previous table, Table 450.3(A) , and see that (A) is for primary over 1000, with two columns for secondaries both over or under 1000V, so that reminds me that Table 450.3(B) is for everything (both) being under 1000V.
 