Dentist office.
We have installed a pvc raceway and floor box for the duplex outlet feeding the dentist chair as we have done 20 plus times for a dentist office.
Inspector failed states it must be a "metal raceway system".
I reread parts of Article 517 and it appears he is correct, and we have been doing it wrong.
Any exceptions I have missed?
Thank you.
We have installed a pvc raceway and floor box for the duplex outlet feeding the dentist chair as we have done 20 plus times for a dentist office.
Inspector failed states it must be a "metal raceway system".
I reread parts of Article 517 and it appears he is correct, and we have been doing it wrong.
Any exceptions I have missed?
Thank you.