On the delta secondary I see no mid-point taps, what point is grounded?
Is it currently intentionally grounded? I cannot see that from the picture.
On the delta, there should be no way for each phase leg to have an equal voltage to ground, as there is no way to have a true neutral, if this is a normal isolation transformer, which it is according to the diagram.
Is it currently intentionally grounded? I cannot see that from the picture.
On the delta, there should be no way for each phase leg to have an equal voltage to ground, as there is no way to have a true neutral, if this is a normal isolation transformer, which it is according to the diagram.