I have a customer that wants a automatic generator installed. Just have a few quick questions.
I'm looking at the generator article in the 2008 nec. It says that the ampacity of the conductors must be 115% of the nameplate rating. This generator is rated at 65 amps. I guessing that means that I will need to run a conductor that can handle a minimum of 75 amps. I will most likely run a #2 SER. Will this be okay?
I also see that it says it will need a disconnect. Don't most automatic generators come with disconnects built in?
I'm looking at the generator article in the 2008 nec. It says that the ampacity of the conductors must be 115% of the nameplate rating. This generator is rated at 65 amps. I guessing that means that I will need to run a conductor that can handle a minimum of 75 amps. I will most likely run a #2 SER. Will this be okay?