I was at a customers house doing electrical work.
When I opened up the 200 amp main breaker panel and 200 amp main lug sub panel along side of it I seen this.
Previous electrical contractor wired this automatic generator transfer like this.
They went from outdoor 200 amp meter main breaker to line side of 200 amp automatic transfer switch with 4/0 ser cable.
Then went from load side of auto transfer switch with 4/0 ser cable to the 200 amp main lug sub panel to the main lugs.
Thats where I was like you got to be kidding me?
It gets worse.
Then they installed a 100 amp 2 pole breaker in sub panel and wired it with #3 copper back to the line side of the 200 amp main breaker in main panel.
Totally wired it backwards.
I called the contractor out on it and he said it was safe and to code?
Come to find out no permit or inspection was done.
I see why?
Please give me you thoughts and feed back.
Thank you
When I opened up the 200 amp main breaker panel and 200 amp main lug sub panel along side of it I seen this.
Previous electrical contractor wired this automatic generator transfer like this.
They went from outdoor 200 amp meter main breaker to line side of 200 amp automatic transfer switch with 4/0 ser cable.
Then went from load side of auto transfer switch with 4/0 ser cable to the 200 amp main lug sub panel to the main lugs.
Thats where I was like you got to be kidding me?
It gets worse.
Then they installed a 100 amp 2 pole breaker in sub panel and wired it with #3 copper back to the line side of the 200 amp main breaker in main panel.
Totally wired it backwards.
I called the contractor out on it and he said it was safe and to code?
Come to find out no permit or inspection was done.
I see why?
Please give me you thoughts and feed back.
Thank you