GoldDigger:
Yes. I was only correcting your comment of 180 deg.
Hysteresis is basically a power loss and therefore can be viewed as a resistive load, but not linear. Its current component will be in phase with the applied voltage.
steve66:
You said the output voltage was 90 deg shifted from the input voltage. This is just not true for a closely coupled transformer. The magnetizing flux is shifted approximately 90 deg from the applied voltage. This flux in turn induces a voltage in the primary coil that opposes the applied voltage, and in turn limits input current. Called a counter EMF. If a second coil, the secondary, is linked to the same flux and wound in the same direction, then the induced voltage is in phase with the primary voltage.
LMAO:
What is special in your autotransformer that you have not described? Is it really just an autotransformer? That is a single magnetic core with a single winding and one tap somewhere along the winding, where the flux density is relatively uniform throughout the core.
.