industrial1003
Member
- Location
- Easton Pennsylvania
I have a utility transformer that appears to be a delta primary, wye secondary (3 hots in, 3 hots and neutral out). Utility was nice enouth to provide me with transformer impedance and X/R ratios to perform the required calculations. I was able to do the calculation for the bolted L-L-L fault at the secondary terminals but do not know how to determine the L-N fault current at the same location considering it is a 3 phase transformer not 1 phase (not sure the single phase transformer formula is applicable as it will result in a much higher AFC and suposidly a 3 phase bolted fault is the worst case condition)? I utilized one of the more simplistic formulas from Cooper Bussmann to perform the L-L-L, but none of their white papers address the L-N fault on a three phase system with the exception of a footnote in one document that said it could be 50 - 125% of L-L-L. Unfortunately I do not have access to any of the IEEE color books that might address this situation and none of the apps I have tried for this show the L-N fault value on a 3 phase system. Any help would be appreciated.