Neither
paul said:Neither
![]()
BryanMD said:you give them a stool to use?
I remember having to bring one from home and getting the hairy eyeball for it.
I don't think the "PlugTail" is intended to be connected/disconnected while the circuit is still hot.frenchelectrican said:for me if i have to remove that kind of device i rather kill the power soruce [ espcally that true with MWBC ] first before ya remove it.
jmsrwd444 said:hey don thanks for coming back on this. i read past 240.4D to 240.4E which discusses tap conductors. i went to 210.19(A) (2) which seems to distinguish for a tap that only connects to one device. i also thought 210.24 (the summary table) lent some credibility to my method as it lists #14 as a tap on a 20amp circuit. i also think 240.21(B)(1)(1)b while this article is specific to feeders it does show code intent for wire to be sized no smaller than capacity of the connected device. thanks for your help jim
John Valdes said:That P&S connector still must be pig tailed to the conductors, so does that really save any time? Plus much more exposed metal. I personally do not back stab and always pig tail. I want all the other recepts to work when one bites the dust.
jmsrwd444 said:hey don thanks for coming back on this. i read past 240.4D to 240.4E which discusses tap conductors. i went to 210.19(A) (2) which seems to distinguish for a tap that only connects to one device. i also thought 210.24 (the summary table) lent some credibility to my method as it lists #14 as a tap on a 20amp circuit. i also think 240.21(B)(1)(1)b while this article is specific to feeders it does show code intent for wire to be sized no smaller than capacity of the connected device. thanks for your help jim
EBFD6 said:I Have to agree with your method, IMO if you are allowed to install 15A recept. on 20A circuit (210.21(b)(3)) , the 6" of #14 you are using as a "TAP CONDUCTOR" is not a violation.
480sparky said:So plug in two 1500w heaters, and what does that do to your #14?
EBFD6 said:What does that do to your 15A receptacle?! Or 20A breaker? Two 1500w heaters is going to be an overloaded 20A recept also. People can and will plug anything in to any size circuit/device/wire, what consumers do with our product after we leave is not the issue here, we have no control over that. I have seen people cut 30A twistlock ends off of cords and install 15A cord cap because the twist lock "wouldn't fit in my outlet" and they called me because they couldn't figure out why the breaker was tripping.
winnie said:when attaching stranded wire to a screw terminal,
480sparky said:I won't do a thing to a 15a receptacle... each heater will draw 12.5 amps, and the receptacle is rated for 15. But there will be 25 amps on the 14, and it's only rated for 15.
peter d said:#14 is rated at 20 amps by T310.16.
Even so, it's still a code violation.
jerm said:You guys use stranded small enough to hook to a 20a receptacle? Anything smaller than 10 we use solid. We sent a pallet of stranded 12 back to the supplier once- they didn't make that mistake again. Stranded 12 just doesn't exist in our world.![]()