Good morning all.
Pool inspection yesterday. Pool panel in detached structure that supplies 4 pumps and various other loads. Previous correction was to provide GFCI protection for pumps and provide main breaker in this panel as more than 6 operations of the hand are required to disconnect all circuits.
Electrician has installed a 2pole 60amp GFCI breaker as the main, and backfed the breaker. Aside from being required to be fastened in place per 408.36(D), can this breaker be used in a backfed configuration? (Murray c/b by the way) The wiring diagram on the Murray website does not show a backfed configuration. I am inclined to require that the GFCI breaker be moved to the source of the pool panel feeder, and a standard 2pole breaker be installed as the main in the pool panel with appropriate fastening. Any thoughts are appreciated..
Pool inspection yesterday. Pool panel in detached structure that supplies 4 pumps and various other loads. Previous correction was to provide GFCI protection for pumps and provide main breaker in this panel as more than 6 operations of the hand are required to disconnect all circuits.
Electrician has installed a 2pole 60amp GFCI breaker as the main, and backfed the breaker. Aside from being required to be fastened in place per 408.36(D), can this breaker be used in a backfed configuration? (Murray c/b by the way) The wiring diagram on the Murray website does not show a backfed configuration. I am inclined to require that the GFCI breaker be moved to the source of the pool panel feeder, and a standard 2pole breaker be installed as the main in the pool panel with appropriate fastening. Any thoughts are appreciated..