SolarNinja
- San Diego, Ca. US
Hello,
I'm currently dealing with the local utility to allow me to tap into their overhead pole mount transformer. This is a property
with 3 parcels and 3 existing meters, of which only 1 can be fed into 18kW roof mount, the rest of my solar 152kW groundmount will need to go into separate meters (aggregate metering with SDG&E). 3phase power is out of the question, there's no infrastructure from utility for 3phase, it's on indian reservation only single phase.
Here's what I'm thinking for the 152kw groundmount
(9) 15kW fronius single phase inverters with Max. OCDP 80amps - That's 720amps of backfeed OCPD
I'm currently working with a service planner that tells me I can add 1 new single 600 amp overhead service.
My question is, and please share your thoughts;
Can I install a main lug 600 amp switch gear and backfeed (9) 80 amp breakers with no main breaker?
Because the sum of the OCPDevices would be 9*80 = 720 amps
600 amp switchgear buss * 1.2 = 720 amps.
So that in my mind is perfect, but there's no main, only a 600 amp service disconnect switch. Will this fly with AHJ?
Thank you in advance.