nickelec

Senior Member
Location
US
Customer called with an issue involving a few ckts. I took a reading at the panel and had intermittent voltage from 100 be on b phase to 140 on a phase
Maybe this was the problem?
cd126fb79c45fd27648462c2ad65eb24.jpg


Sent from my SM-G950U using Tapatalk
 
Last edited by a moderator:
Customer called with an issue involving a few ckts. I took a reading at the panel and had intermittent voltage from 100 be on b phase to 140 on a phase
Maybe this was the problem?
cd126fb79c45fd27648462c2ad65eb24.jpg


Sent from my SM-G950U using Tapatalk

Was that the meter base for shore power for the Titanic?

For the sake of others finding this topic in the future, perhaps a mod can change "nutreal" to "neutral".
 
Sorry.. but that was the issue. Changed out meter pan and all was well again

Sent from my SM-G950U using Tapatalk
 
It looked like it was getting wet

Sent from my SM-G950U using Tapatalk
Looks like SE cable - take a look at the other end of the cable - I'd bet there isn't sufficient enough drip loop or "gooseneck" and water is entering that end and running down inside the cable and ending up on terminations. Could even have compromised jacket along the cable - you should have fixed or replaced this or it will happen again, though it may take another 20-50 years before it fails again.
 
There used to be a separate meter for the hot water heater that's not in use any more
c30f7b3ca0aacfad3fede892c8087a35.jpg
5c049af43acd38df94df9ea2313c353a.jpg


Sent from my SM-G950U using Tapatalk
Some POCOs provided a lower rate per kWh for water heating. Others ran the lower element of water heater off the combination of separate meter and off-peak time clock.