Are you sure it is NM cable and not SE cable/conductors?Terminating 2 existing 3 wire NM cables in a newly installed residential sub panel. One for range one for clothes dryer.
I would say they should terminate on the neutral bar and not the equipment ground bar.
Is that correct.
Thanks
The 3 wire range and dryer circuits were only allowed to the main panel, not a sub-panel. If it's now a sub-panel they need to be upgraded to 4 wire.Terminating 2 existing 3 wire NM cables in a newly installed residential sub panel. One for range one for clothes dryer.
I would say they should terminate on the neutral bar and not the equipment ground bar.
Is that correct.
Thanks
They were allowed if the grounded conductor was insulated. The grounding conductor in NM cable was never permitted to be used as a grounded conductor no matter where the circuit originated.The 3 wire range and dryer circuits were only allowed to the main panel, not a sub-panel. If it's now a sub-panel they need to be upgraded to 4 wire.
I stand corrected. The range is SE cable.Are you sure it is NM cable and not SE cable/conductors?
As for the EM disconnect, you can label it "emergency disconnect, not service" and not have to run a 4-wire.