Jim: The ventless fans do not comply. Exhaust must be directly dicted to the exterior of the building.Originally posted by jimwalker:
Ok if that fart fan is to indeed remove methane gas ,please exsplain the ventless ones!!!!!
I would think that if methane were a concern, it certainly would have been noted when all of the bathrooms were engineered across this country.NFPA 820
Standard for Fire Protection in Wastewater Treatment and Collection Facilities
7-2.2
Ventilation systems serving hazardous areas classified under the provisions of Article 500 of NFPA 70, National Electrical Code, shall incorporate fans fabricated in accordance with Air Moving and Control Association (AMCA) Type A or Type B spark-resistant construction.
Jim: Put a mirror in your wet bar, kitchen and laundry room and see how long it takes to fog up. Let me know in a few years when it actually does. Also, the rooms you point out above must meet a minimum of 4% natural ventilation and 8$ natural light (based on square footage), bathrooms do not.Originally posted by jimwalker:
[QB] Ryan i havn't seen a ventless in years .Was only using it to prove a point about gas.How can our laundry room ,wet bar or kitchen be safe if that is what this fan is all about.
NFPA 5000
51.3.2.12.4 Bath Ceiling Units. Bath ceiling units providing any combination of heat, light, or ventilation shall be provided with controls that allow separate operation of each function. In an assembly that is part of the building envelope, they shall be insulated to the outside in accordance with 51.3.2.2.