ARTICLE 210.11(C)(3)Bathroom Branch Circuits.In addition to the number of branch circuits required by other parts of this section,at least one 20-ampere branch circuit shall be provided to supply bathroom receptacle outlet(s). Such circuits shall have no other outlets.
I do not see that you can feed three bathrooms with one 20 amp circuit.
in the Exception on the next page.
Where the 20 amp circuit suplplies a single bathroom, outlets for other equipment within the same bath room shall be permitted to be supplied in accordance with 210.23(A)(1)and (A)(2)
so i would say you need three 20 amp circuits for three bathrooms.
If you take a single 20a circuit to three receptacles in 3 bathrooms, that's legal.
As soon as you hook something else up in one of the bathrooms to that circuit, such as a bath fan or towel warmer or in-wall heater or light, then that circuit cannot be taken to any other bathroom. You must have another 20a circuit to feed the other two.
Now, if you hook up a bath fan or towel warmer or wall heater or light in either of those two baths, you now must 'dedicate' that circuit to that bathroom, and you need yet another 20a circuit for the third bathroom.
But you can legally take one 20a bathroom circuit and feed 50 bathrooms (yea, it's gonna be one big house!) that have 5 receps each, as long as it only feeds those 250 receps.
The last sentence of 210.11(C)(3)states that,"Such circuits shall have no other outlets".
It does not say you can feed multiple bathrooms with one circuit.
Can you point out where in the 2008 NEC that says that you can feed more than one bathroom with the required 20 amp circuit for the outlet?
210.11(C)(3) Bathroom Branch Circuits. In addition to the number of branch circuits required by other parts of this section, at least one 20-ampere branch circuit shall be provided to supply bathroom receptacle outlet(s). Such circuits shall have no other outlets.
Where does it say anything about ONE bathroom per circuit?
Such circuits shall have no other outlets.
The very last sentance.
![]()
Legal. I have one circuit feeding the receptacles in 4 bathrooms. It has no other outlets. I have complied with 210.11(C)(3).
As usual the code does not make it perfactly clear and 210.11(C)(3) is no exception
Here is what i would do, run 3 -20 amp circuits one for each bath room GFCI,
And one 20amp circuit for lights and exaust fans in all 3 bathrooms.
now the inspector cannot flag me for the last sentence of 210.11(C)(3)
And i have been flaged for daisy chaining the gfci circuit from one bath to another .
The last sentence is perfectly clear. I can't use the 20a bath circuit for anything but the receps. If I do (according to the exception), then I can't have that circuit feed anything outside the bath.
Why a 20a circuit for the lights & fans? I usually use a local 15-a general purpose circuit for that.
As for daisy-chaining one bath to another, either your inspector needs educated, or you have a local code.
........I do not agree with the inspector but he has the authority and i do not find his request unreasonable.The mass Electrical code does not address this issue...............
............The inspector sites the last sentance of 210.11 (C)(3) as the reason for the home run for each bathroom gfci circuit.
As usual the code does not make it perfactly clear and 210.11(C)(3) is no exception
Here is what i would do, run 3 -20 amp circuits one for each bath room GFCI,
And one 20amp circuit for lights and exaust fans in all 3 bathrooms.
now the inspector cannot flag me for the last sentence of 210.11(C)(3)
And i have been flaged for daisy chaining the gfci circuit from one bath to another .
If you have been flagged for an install like 480sparky drew then your inspector is not correct. I agree with Ken it is perfectly clear.
No, the inspector does not have the authority. That would be the AHJ, which will be further up the chain of command. Inspectors are in enforcement and cannot legally make up codes any more than police officers can make up laws.
Then he's dead-arse wrong. Given the chance, I'll challenge him.
So as you can see the inspectors request is not that unresonable after all.
Leo, show this to your inspector and see if he will admit he is wrong.So as you can see the inspectors request is not that unresonable after all.
............the last sentence of 210.11(C) (3) "SHALL HAVE NO OTHER OUTLETS"
...............
Leo, show this to your inspector and see if he will admit he is wrong.
![]()
Anyone who wires bath lights & fans like that should be shot, hung, drawn & quartered and placed on a rack.![]()
Please explain...![]()