220.52(C) Bathroom Circuit Load. A load of not less than 1500 volt-amperes shall be included for each 2-wire bathroom receptacle branch circuit installed as required by 210.11(C)(3). This load shall be permitted to be included with the general lighting load and subject to the demand factors provided in Table 220.42.
Substantiation:
The small appliance and laundry circuits are required to be used for load calculations, why not the bathroom receptacle circuit?
220.52(C) Bathroom Circuit Load. A load of not less than 1500 volt-amperes shall be included for each 2-wire bathroom receptacle branch circuit installed as required by 210.11(C)(3). This load shall be permitted to be included with the general lighting load and subject to the demand factors provided in Table 220.42.
Substantiation:
The small appliance and laundry circuits are required to be used for load calculations, why not the bathroom receptacle circuit?