- Location
- Chapel Hill, NC
- Occupation
- Retired Electrical Contractor
chris kennedy said:402.5 "allowable amp. fixture fixture wires. Thhn is not in this table. Therefore its a branch cir., IMO.
You are on a roll Chris but I think you mean Table 402.3
chris kennedy said:402.5 "allowable amp. fixture fixture wires. Thhn is not in this table. Therefore its a branch cir., IMO.
Isn't the wire going to the fixture part of the branch circuit?Dennis Alwon said:Art. 402 is called Fixture Wires. Where are you going with this Celtic?
240.5 Protection of Flexible Cords, Flexible Cables, and Fixture Wires.
Flexible cord and flexible cable, including tinsel cord and extension cords, and fixture wires shall be protected against overcurrent by either 240.5(A) or (B).
Flexible cords and cables, because of the nature of their use, are not considered to be wiring methods. Wiring methods are covered in Chapter 3 of the Code. Careful study of 400.7, Uses Permitted, and 400.8, Uses Not Permitted, is required before choosing flexible cords or cables for a specific application.
What are they then ?M. D. said:What they are not is branch circuit wiring.
chris kennedy said:Doesn't say Thhn in FMC.
chris kennedy said:Doesn't say Thhn in FMC.
Dennis Alwon said:I agree. It is a code violation (IMO) whether the fixture wire is a branch cir. conductor or not.
celtic said:I seem to have gotten lost here....when did THHN and FMC come into the picture![]()
celtic said:What are they then ?
Necdigest ?, February 2007
Compiled by Jeff Sargent and the NFPA Electrical Engineering Team
Q. Can I use 14-2 wire for the switch leg of a light fixture where the branch circuit is protected by a 20-amp circuit breaker? If this is against Code, why can I use 15-amp switches and receptacles on 20-ampere circuits?
A. The conductors from a switch location to the lighting outlet it controls are considered branch circuit conductors, not tap conductors connected to branch circuit conductors. These conductors are subject to the general overcurrent protection requirements of Section 210.20(B), which points to Section 240.4 for the specific overcurrent protection requirement. Section 240.4(D) specifies that 14 AWG copper conductors are to be protected by an overcurrent protective device with a rating or setting no higher than 15 amperes. And Table 210.24, which summarizes the requirements for branch circuits with two or more outlets or receptacles, specifies that the minimum conductor size for a 20-ampere-rated branch circuit is 12 AWG......
Dennis Alwon said:Article 402 Table 402.3 Fixture Wires
It lists all the fixture wires. Chris was saying THHN, the 14/2 nm that Trevor used, was not listed as a fixture whip.
M. D. said:What they are not is branch circuit wiring.
celtic said:What are they then ?
M. D. said:Fixture wiresDid the wires Trevor installed come with fixture? clue one.
infinity said:The feed to the light is about 4' of #14 NM cable.
celtic said:HUH??
I know what your position is (14/2 is not legal) and I do agree, but unless I missed the sarcasm ~ HUH???